I have a water pump that I am running that keeps blowing a 20 amp fuse in my house. The pump requires "a 15 amp dedicated outlet for proper operation". Although its a newer house I notice that the electrical wiring might not be too good, I blow fuses if I run two 1500 watt space heaters in the same room. I am electrically challenged so please forgive my ignorance. What options do I have to fix this problem?
 

917601

Mother Lode Found
Mother Lode
Joined
Apr 2, 2010
Messages
11,250
Likes
9,250
#2
I have a water pump that I am running that keeps blowing a 20 amp fuse in my house. The pump requires "a 15 amp dedicated outlet for proper operation". Although its a newer house I notice that the electrical wiring might not be too good, I blow fuses if I run two 1500 watt space heaters in the same room. I am electrically challenged so please forgive my ignorance. What options do I have to fix this problem?
Off hand? I would run the pump and check the amps it is pulling. Get a cheapo voltmeter and connect it up in series with the pump, read the amps it is using, if more than 15 amps, that is your problem, also a sign your pump is going tits up.
 

southfork

Site Supporter
Site Supporter
Mother Lode
Joined
Mar 31, 2010
Messages
14,550
Likes
12,768
#3
I have a water pump that I am running that keeps blowing a 20 amp fuse in my house. The pump requires "a 15 amp dedicated outlet for proper operation". Although its a newer house I notice that the electrical wiring might not be too good, I blow fuses if I run two 1500 watt space heaters in the same room. I am electrically challenged so please forgive my ignorance. What options do I have to fix this problem?
You cant run 2 1500 watt space heaters on one circuit, the max is 1500 watts for a #14 line witch is normal, it carrys a 15 am cb which is standard, bathrooms may carry a 20 amp but your still limited on the wattage, regarding the pump it's possible they did not place it on a dedicated line, sometimes they place the garage outlets on it too and if you have a fridge as some do it will still blow, its possible also the cb is bad.
 

Silver Buck

Gold Member
Gold Chaser
Joined
Oct 22, 2010
Messages
2,377
Likes
1,475
Location
Western Shores of Lake Erie
#4
I have a water pump that I am running that keeps blowing a 20 amp fuse in my house. The pump requires "a 15 amp dedicated outlet for proper operation". Although its a newer house I notice that the electrical wiring might not be too good, I blow fuses if I run two 1500 watt space heaters in the same room. I am electrically challenged so please forgive my ignorance. What options do I have to fix this problem?
It's been a bit, so forgive my rustiness and accuracy.

Power = Current x Voltage.

therefore

Current = Power / Voltage

Power = 1500 Watts x 2 (your heaters) = 3000 Watts
Voltage = 120 Volts

Current = 3000 Watts (or Volt-Amps) / 120 Volts = 25 Amps. Definitely too much for your 20 Amp circuit.

However, since we're talking AC power, I believe that we multiply that 25 Amps by .707 (I don't remember if the 120 is peak AC or RMS/Average).

So, let's see what we come up with.

25 Amps x .707 = 17.68 Amps

That's a bit close to that 20 Amp fuse you're blowing (provided that you are running those heaters on Max). Add anything else to that circuit the 20 A fuse is sure to go.

Doing a bit of Googling, it seems that my 25 Amp answer is correct (12.5 Amps per heater).

http://robbieselectrical.com/breakers.html

As far as your pump goes, it could have some windings shorted out to have it draw excessive current. Or perhaps there are other devices active on that circuit which pushes the current to flow through it to go past 20 Amps.

Hope this helps.
 

917601

Mother Lode Found
Mother Lode
Joined
Apr 2, 2010
Messages
11,250
Likes
9,250
#5
As mentioned here on previous posts, check CB, remove it and check the contacts on the buss bars. I had the same problem with a house circuit. I pulled the CB out and there was HUGE amounts of powdery corrosion on the CB contact points and breaker bar. I brushed the bar free of powder and replaced the Circuit breaker. Careful, the bars, ( the part that the CB snaps to, is LIVE unless you cut the power to the breaker box). Also, you will have to pull the CB box cover off to remove the individual CB, be careful.
 

Irons

Deep Sixed
Mother Lode
Site Supporter ++
Joined
Mar 30, 2010
Messages
25,191
Likes
36,923
#6
Electricity and I have an agreement. I don't mess with it and it doesn't kill me.
 

dollars

New Member
Joined
Mar 31, 2010
Messages
21
Likes
3
#7
However, since we're talking AC power, I believe that we multiply that 25 Amps by .707 (I don't remember if the 120 is peak AC or RMS/Average).

Brings back memories I believe the 120 volts ac is already RMS

I would check how the pump runs on a dedicated circuit

if there are continued problems I would check the current drawn compared with the motor name plate full load rating

This may help to verify if the pump/motor is faulty (ie breaings on the way out etc) or possible other problems with wiring/circuit breaker/fuse etc

stay safe
 
Joined
May 20, 2012
Messages
1,683
Likes
1,348
Location
Some place
#8
Is it a fuse or a breaker?

If it's a breaker it could be old and worn out.

If it's a fuse they are kind of expensive to replace so put a penny in place of the fuse.
 

MrLucky

Silver Member
Silver Miner
Site Supporter
Joined
Apr 27, 2011
Messages
997
Likes
478
Location
On the Fortuna II
#9
Although its a newer house I notice that the electrical wiring might not be too good.
Since you already suspect the wiring in your house, I'm going to throw in another consideration. How far away is the pump (feet)? Is it possible the wire is undersized for the distance?
 

Unca Walt

Midas Member
Midas Member
Joined
Mar 15, 2011
Messages
7,085
Likes
7,884
Location
South Floriduh
#10
As an ole electricabibble type, I just gotta say that ALL the answers here are spot on. ('Cept Publico, and he's teasin')

Silver Buck: Yer spot on alla way down the line. But I've got a nagging memory from decades (too dang many decades!) back... that is, somehow I remember that FUSES were not rated at .707 (Root Mean Square for the non-elec dudes <-- means since there are gaps betwixt sine waves, ya haveta mathematically "flatten them" to see what the "constant current" is) but at the equivalent of DC.

The reason for this, IIRC, is most folks see 120V, see 10A, and know the basic power formula (Duh: 120 X 10 = 1200W <-- NOT 848 W). So the custom was to use those straight numbers for fuses.

Alla that said. I could be fulla sh!t. :cheerful::thumbs_up:

Really doesn't make. OP should be happy as a demented goat, 'cause if'n that fargin fuse didn't blow, yer 24 gauge wire will eventually become a long, hot filament.

And I agree: If you've got coils that are now shorted (but the pump still pumps), you are gonna draw a lotsa more current.


LATE SANITY EDIT: :bowdown::bowdown: Dollars:bowdown::bowdown: straightened out my memory!!!! He is right! 120V IS the RMS. The AVERAGE would be less (.637 X 120)
 
Last edited:

itsamess

Gold Member
Gold Chaser
Site Supporter
Joined
Jan 4, 2013
Messages
667
Likes
662
#11
If plugged into outlet you might want to buy a Kill a watt plug in meter (cheap, safe and great for checking draw on older appliances or your infrared heaters). They are about $20 here or HD etc
82-715-001-05.jpg

If initial draw is high at first on then drops off a cheap option is to install start capacitor like on ac compressor units. These are also great for lowering startup draw for running items off generators.
 

00nightstorm

Seeker
Seeker
Joined
Mar 31, 2010
Messages
293
Likes
183
#12
It trips the breaker plugged into any outlet. The outlet it is plugged into right now is about 25 ft away from the fuse box. The manufacturer said it will run fine plugged into any normal wall outlet but that does not look like the case. Maybe the motor is out of wack. It looks like I will probably have to have a dedicated line installed. No idea what that will cost but a local electrician is coming by here tomorrow afternoon to take a look and give me an estimate. Maybe I will have him see how much the draw is on the motor first? Thanks for all the advice guys...
 

00nightstorm

Seeker
Seeker
Joined
Mar 31, 2010
Messages
293
Likes
183
#13
If plugged into outlet you might want to buy a Kill a watt plug in meter (cheap, safe and great for checking draw on older appliances or your infrared heaters). They are about $20 here or HD etc
View attachment 55791

If initial draw is high at first on then drops off a cheap option is to install start capacitor like on ac compressor units. These are also great for lowering startup draw for running items off generators.
I never run it for longer than 10 minutes and often times it does not trip the breaker at all. Other times it will trip it in about 15-30 seconds.
 

southfork

Site Supporter
Site Supporter
Mother Lode
Joined
Mar 31, 2010
Messages
14,550
Likes
12,768
#14
It trips the breaker plugged into any outlet. The outlet it is plugged into right now is about 25 ft away from the fuse box. The manufacturer said it will run fine plugged into any normal wall outlet but that does not look like the case. Maybe the motor is out of wack. It looks like I will probably have to have a dedicated line installed. No idea what that will cost but a local electrician is coming by here tomorrow afternoon to take a look and give me an estimate. Maybe I will have him see how much the draw is on the motor first? Thanks for all the advice guys...
Your pumps not on an extension cord is it? If so that could be the problem having an undersized cord.
 

Rusty Shackelford

Midas Member
Midas Member
Site Supporter
Joined
Apr 1, 2010
Messages
6,075
Likes
4,133
Location
Northern most Southern State
#15
Surprised that no one mentioned going redneck and use a bigger fuse!!

Curious, what newer home uses fuses? I would have assumed any newer home would be protected by breakers.
 

Goldhedge

Moderator
Site Mgr
Sr Site Supporter
Joined
Mar 28, 2010
Messages
30,497
Likes
37,183
Location
Planet Earth
#16
From my limited knowledge on the subject...


Typically houses have 14ga wire and 15A circuits (for lights and plugs NOT the heavy appliances washer/fridge etc. they're usually 12ga/20A. The electric stove is 220vac)


Commercial has 12ga wire and 20A circuits.


But if you have an electrician coming over, pick his brain on the subject...
 
Joined
May 20, 2012
Messages
1,683
Likes
1,348
Location
Some place
#18
As an ole electricabibble type, I just gotta say that ALL the answers here are spot on. ('Cept Publico, and he's teasin')
I am not teasin'. A breaker rated at 20 amps can get "pleasure bent" to engage at a lower amperage.

And the replacing a fuse with a penny solves the problem with a new house paid for by the home owner's insurance payout.
 

TN_Preacher

Silver Member
Silver Miner
Joined
Jan 28, 2013
Messages
140
Likes
149
Location
Tennessee
#19
I have a water pump that I am running that keeps blowing a 20 amp fuse in my house. The pump requires "a 15 amp dedicated outlet for proper operation". Although its a newer house I notice that the electrical wiring might not be too good, I blow fuses if I run two 1500 watt space heaters in the same room. I am electrically challenged so please forgive my ignorance. What options do I have to fix this problem?
You need to describe your situation better... Is it a sump pump? A septic tank pump? And if it is a newer house, you have all breakers, not fuses, correct? The breaker is doing what it is designed to do when you are running 3000 watts (25 A) on a circuit designed for only 20 A. One heater is all you should run on that circuit.

"Dedicated circuit" means that there should be nothing else on the same circuit, because the water pump requires all the current that the circuit can supply. I would definitely use a 20 A circuit (12 AWG) in that situation.

If you are blowing a breaker on the sump pump, see if the breaker is on a GFI circuit. If so, then there is current flowing to ground, meaning that somewhere in the circuit the insulation may be breaking down. Breakers also fail, the metal fatigues over time, contacts corrode, etc. Pump motors also fail.

Please describe your circuit the best you can, and if you don't know what something is called, take a picture and post it. Like Johnny 5 says... 'need input.'


 
Last edited by a moderator:

Spectrism

Seeker
Seeker
Joined
Oct 31, 2012
Messages
329
Likes
300
Location
In the NE part of the MATRIX
#20
If your fuse or breaker is rated for the load, a tripped circuit means you have a short somewhere.... or, you are not getting a proper power feed. Someone mentioned corrosion on the main bar or a fuse holder. If you have corrosion at connecting parts of the feed line, they act as resistance. At resistance there is a voltage drop. When a load is pulled, the voltage supplied to that load will drop severely.

Let's say you have a 120VAC pump. It wants to use 3000 Watts. The current draw will be:
3000/ 120 = 25 amps.

Let's say there is corrosion or a broken wire feeding this line. When the pump is turned on, instead of seeing 110 or 120VAC to feed the 3000Wts, it drops down to 90 volts. Here is what it does to the current:

3000/ 90 = 33.3 amps.

Fuses trip on current.



DO NOT get a cheap "voltmeter" and hook it up in series with the pump. You will surely let smoke out of the voltmeter that should never come out. You will likely see fireworks too.

Measure volts first. It is easier and safer. If you want to measure current, get a current sensor that goes around the wire. If you are not sure about what you are doing, don't do it. You don't get second chances.
 

andial

use default title
Midas Member
Site Supporter ++
Joined
Apr 1, 2010
Messages
10,428
Likes
10,639
#21
I am in full agreement with what numbers posted, in post #2 .
 

obilly

Silver Member
Silver Miner
Joined
Mar 31, 2010
Messages
614
Likes
410
#22
i would think you have a queer breaker if it keeps blowing fuses?
 

JustPassinThru

Gold Member
Gold Chaser
Joined
Dec 13, 2011
Messages
2,736
Likes
1,535
Location
a better place
#23
I was going to suggest the one-cent solution, but Publico beat me to it.

It does have some things to recommend it. Cheap initial outlay, and a very, VERY permanent solution. At minimal cost to you, but...a bit inconvenient.
 

ttazzman

Midas Member
Midas Member
Site Supporter ++
Joined
Apr 2, 2010
Messages
4,816
Likes
4,246
Location
mid-usa
#25
really need to know the pump motor size.....

but its highly possible the pump STARTER is weak or out...

pump motors have a high starting amp draw.....then lower to run...

A. assuming the pump worked at sometime on the circut in question...then

#1...a starter problem or a load problem has developed in the pump (replace pump..or starter...or brushes etc.)
#2 ...the pump is fouled and overloading on startup (clear fouling)(make sure pump is free and turns)
#3....the circut breaker is getting weak...(replace with delayed trip breaker)

B. the pump is new to you and never been run by you before..

#1 and #2

#3 your home circuts are not rated for the pump starting/running load (consult label on pump motor to determine)

FWIW...pump motor starting loads can be as high as 2.5 times running loads

Since you state your pump requires 15amps to run....any modern home under 20yrs old should have that (15amp) as a minimum circuit capacity, would be good to make sure not much else is on the circut

if it is blowing while runing on a 20amp breaker as you state.......its probably something else on the circut cycling such as a deep freeze ..etc..
 
Last edited:

Ragnarok

I'd rather be
Midas Member
Joined
Mar 31, 2010
Messages
5,537
Likes
4,382
#26
Best to keep the load on a fuse/breaker to about 75% of its rating imho (15amps max on a 20amp fuse/breaker).

And imho no discussion about fuses should be without this handy guide: ;)

Fools Guide to Fuse Replacement.jpg

2c,
R.
 
Last edited:

brosil

Gold Member
Gold Chaser
Site Supporter
Joined
Mar 31, 2010
Messages
2,183
Likes
1,832
Location
Oak Harbor, Ohio
#27
I had a similar problem once and replaced the breaker with a hi-mag breaker. They will accept a higher starting current. It does kind of sound like a cheap starting cap on the motor, though.
 

Unca Walt

Midas Member
Midas Member
Joined
Mar 15, 2011
Messages
7,085
Likes
7,884
Location
South Floriduh
#28
I am not teasin'. A breaker rated at 20 amps can get "pleasure bent" to engage at a lower amperage.

And the replacing a fuse with a penny solves the problem with a new house paid for by the home owner's insurance payout.
(*snork*) Hadn't thought of that... butcha better tell the OP to remove the penny after the house is gone but the insurance guy has not shown up yet. :s13:
 
Joined
May 20, 2012
Messages
1,683
Likes
1,348
Location
Some place
#29
(*snork*) Hadn't thought of that... butcha better tell the OP to remove the penny after the house is gone but the insurance guy has not shown up yet. :s13:
If the OP isn't smart enough to remove the penny before the insurance adjuster shows up then the OP isn't smart enough to deserve an insurance settlement.
 

00nightstorm

Seeker
Seeker
Joined
Mar 31, 2010
Messages
293
Likes
183
#30
The electrician told me the problem was arc-fault breakers. I have some GFI breakers at a few locations in the house so I will just run an extension cord to one of these to run the pump while I am out of town.
 

SWRichmond

Silver Miner
Seeker
Joined
Mar 31, 2010
Messages
502
Likes
428
#32
I have a water pump that I am running that keeps blowing a 20 amp fuse in my house. The pump requires "a 15 amp dedicated outlet for proper operation". Although its a newer house I notice that the electrical wiring might not be too good, I blow fuses if I run two 1500 watt space heaters in the same room. I am electrically challenged so please forgive my ignorance. What options do I have to fix this problem?
If the pump used to work ok and not pop the breaker, then you should probably suspect the pump motor is starting to go bad and is drawing more current than it was when it was newer.
 

TN_Preacher

Silver Member
Silver Miner
Joined
Jan 28, 2013
Messages
140
Likes
149
Location
Tennessee
#33
The electrician told me the problem was arc-fault breakers. I have some GFI breakers at a few locations in the house so I will just run an extension cord to one of these to run the pump while I am out of town.
If you want to be sure the pump won't fail when you are out of town, make sure it has a battery backup with sufficient capacity for the duration of your time away. GFCIs are known to trip when used with water pumps just like arc-fault breakers can trip with motors.
 

CiscoKid

They all look good through beer goggles...
Gold Chaser
Joined
Nov 30, 2010
Messages
2,632
Likes
2,370
Location
Between here and there
#34
The electrician told me the problem was arc-fault breakers. I have some GFI breakers at a few locations in the house so I will just run an extension cord to one of these to run the pump while I am out of town.
I had some of those GFI breakers start to go bad on me and was told by an electrician that I trust that they were crap and that hardly anyone uses them any longer. The smart setup is to run a standard breaker and have the first outlet in the circuit be a GFI outlet. Replaced the GFI breakers and never had another issue. Also, what Publico says about breakers getting weak after so many trips is true. At least, in my experience. And, for what it is worth, I never waste time installing anything less than 20 amp breakers with 12 gauge wiring and I install a fair amount of new electric.
 

southfork

Site Supporter
Site Supporter
Mother Lode
Joined
Mar 31, 2010
Messages
14,550
Likes
12,768
#35
Did he mean an arcing gfi breaker, gfis's are very fussy and go bad, check to see what wire size you have, if its #12 make sure they have a 20amp gfi installed, some builders are cheap and will use a 15gfi on a #12 wire.
 

TN_Preacher

Silver Member
Silver Miner
Joined
Jan 28, 2013
Messages
140
Likes
149
Location
Tennessee
#36
Did he mean an arcing gfi breaker, .
The arc fault breaker is a relatively recent requirement of the NEC, required for all bedrooms in residential dwellings. They are designed to prevent fires due to bad connections (hence arcing), but they are prone to nuisance tripping,which I believe was the issue with the OP.